Achieving good precision with currents of less than 5 A

 I'm considering building an energy monitor based on the Open Energy Monitor design for the purposes of determining power dissipation of some computers in a cabinet. The power information would then be used in a feed-forward control system to predict how much cooling effort is required - as opposed to a feed-back control system where the system waits for it to get too hot before applying more cooling effort.

For my requirements I think I need good resolution up to 4 A (about 1000 W) so I was considering using a more suitable CT than the usually recommended 30 A CTs.  At the moment I'm looking at an AC1005 5A current transformer <http://www.amveco.com/pdf/AC1005.pdf>.  Do you think this can be made to work with the Open Energy Monitor design given appropriate adjustments to the value of the burden resistor?  I realise I need to break into the mains circuit to do that since this isn't a clip-on CT, but I'm perfectly comfortable with mains voltage work.

Alternatively, does anybody have experience with using a current transformer such as the SCT-013-030 which is good for up to 30 A, but  with multiple turns on the primary in order to increase sensitivity. By looping the primary through six times can I use the SCT-013-030 as a 0 to 5 A transformer rather than a 0 to 30 A transformer?

Thanks,

Rob

 

glyn.hudson's picture

Re: Achieving good precision with currents of less than 5 A

 Hi Rob,

Sounds like an interesting project. You are already thinking along the right lines, you will get better precision using a CT designed for lower power levels. 

Have you seen this page: http://openenergymonitor.org/emon/node/156 ? The calculations at the bottom of the page runs through the process of calculating a value for the burden resistor depending on how many turns the CT has an over what range you wish to measure. 

The AC1005 CT should work fine. The SCT-013-030 CT has actually got a built in burden resistor and gives a voltage output. See datasheet here: http://www.seeedstudio.com/depot/noninvasive-ac-current-sensor-30a-max-p-519.html?cPath=144_154

Hope this is helpful, let us know how you get on

All the best, Glyn. 

Comment viewing options

Select your preferred way to display the comments and click "Save settings" to activate your changes.