Hi,
It's possible to use shematic for non invasive 3.0 without voltage measurement ?
It makes sense or not?
If yes, how adapt the code ?
Regards.
Archived Forum |
|
Non invasive 3.0 w/h voltage measurementSubmitted by Guest on Sat, 03/12/2011 - 11:12Hi, It's possible to use shematic for non invasive 3.0 without voltage measurement ? It makes sense or not? If yes, how adapt the code ? Regards. » |
Re: Non invasive 3.0 w/h voltage measurement
Yes, you can use just the CT to make apparent power measurements assuming PF=1 and assuming the voltage is constat. The emonTx firmware example does just this. Just strpip our the RFM12B wireless code if it is not required: https://github.com/openenergymonitor/emonTxFirmware/tree/master/emonTx_SingleCT_Example_
Re: Non invasive 3.0 w/h voltage measurement
I will try that, thanks for information :).
Re: Non invasive 3.0 w/h voltage measurement
Hi
Variable "emontx.supplyV" is used in the calculation.
If voltage is constant, I have to set it to 1 ?
Regards