Hi, I've been reading the documentation here on OEM for the past couple of days and its really insightful. Thank you for putting this out here.
For the current measurement, I'm using a Bourns 53150C current transformer with a turns ratio of 1:150. Datasheet is available here. This is rated for 10A maximum current. Now my ADC can tolerate upto 1.5V on its input and hence for the rated current of 10A I need to output 1.4V. This gives me the R(burden) value of 21R.
Hence,
Current Constant = (10 ÷ 66.67m) ÷ 18 = 8.333.
[Isec = Ipri x Npri/Nsec = 10 x 1/150 = 66.67m]
Is this calculation correct?
Also I don't quite understand how this line in the voltage constant description is derived:
voltage constant = 230 × 11 ÷ (9 × 1.20) = 234.26
Any help would be really appreciated!
Re: Calibration constants
It is all spelled out in the Building Blocks page about Calibration theory. It's only the voltage ratio from your ac adapter = 230 ÷ (9 × 1.20) and the voltage dividers (11)!