Configure EmonTx for High Current Measurements

Hi,

I'm wondering if someone can configure the EmonTx node to work with high current sensor (SCT-2000-1500)?

I'm working in a research project to measure Power Box current, and we're trying to use EmonTx for this purpose.

 

Many Thanks

Thamir

 

Robert Wall's picture

Re: Configure EmonTx for High Current Measurements

You will need to order your SCT-2000-1500 with a 1 V rms output and remove the burden resistor in the emonTx (or choose the version without an internal burden and supply your own external burden or change the internal burden to the correct value), and change the calibration factor. Your problem is exactly the same as that faced by users in the USA, so read that Building Blocks page.